The NEC states that equipment grounding conductor should be sized according to the rating of the overcurrent device feeding the equipment.
It seems like the logic is that in event of a fault within the motor causing ground current to flow in equipment ground conductor, we want the cable to be protected over a range of time and currents that is bounded by the protection. i.e. the motor must trip before the cable melts.
From that logic, should we be permitted to use much smaller grounding conductors for motors that are protected by sensitive ground fault relaying?