I am looking for a litle guidance about somthing that is driving me crazy whilst trying to size a motor conductor/fuse combination (Using NEC Code).
I have a 75HP AC motor (regular NEMA frame 1.15 SF)with seperate O/L protection so the fuse is SC and GF protection only and I want Type 1 coordination. So I use the FLA from the NEC tables = 96A, my branch circuit conductor MINIMUM size must be at least 125% FLA capable = 120A min so 1AWG (75degree C rating) However the application is for "heavy" start so i can increase the fuse the to 225% (Time delay RK5 Type)so potentially I can use a 2.25 x 96 = 216A say 200A fuse. The question is can my conductor still remain as 1AWG OR should the conductor always be rated higher than the capacity of fuse rating. I am thinking that I can use the 1AWG as the idea is the fuse will blow before the cunductor has time to melt (as the code/fuse/cable insulation has all been carefully planned to work that way (ha!)) and I cannot find a statement that says "the conductor size must be larger than the fuse capacity". But my real feeling is that it should be.
Another related issue is I see a lot of the larger cables in control panels (like from main disconnects and distribution blocks) that are the high temperature (200deg c)type that look like they have been sized directly with the current capacity in mind and not the fact that the terminal max temp capacity maybe only 75degc. (ie neglecting the fact that the terminal needs the copper content of a lower temp rated cable todisspiate the heat at the terminal hence a larger cable size regardless of capacity) Has anyone out there been caught out by this ?
I have a 75HP AC motor (regular NEMA frame 1.15 SF)with seperate O/L protection so the fuse is SC and GF protection only and I want Type 1 coordination. So I use the FLA from the NEC tables = 96A, my branch circuit conductor MINIMUM size must be at least 125% FLA capable = 120A min so 1AWG (75degree C rating) However the application is for "heavy" start so i can increase the fuse the to 225% (Time delay RK5 Type)so potentially I can use a 2.25 x 96 = 216A say 200A fuse. The question is can my conductor still remain as 1AWG OR should the conductor always be rated higher than the capacity of fuse rating. I am thinking that I can use the 1AWG as the idea is the fuse will blow before the cunductor has time to melt (as the code/fuse/cable insulation has all been carefully planned to work that way (ha!)) and I cannot find a statement that says "the conductor size must be larger than the fuse capacity". But my real feeling is that it should be.
Another related issue is I see a lot of the larger cables in control panels (like from main disconnects and distribution blocks) that are the high temperature (200deg c)type that look like they have been sized directly with the current capacity in mind and not the fact that the terminal max temp capacity maybe only 75degc. (ie neglecting the fact that the terminal needs the copper content of a lower temp rated cable todisspiate the heat at the terminal hence a larger cable size regardless of capacity) Has anyone out there been caught out by this ?