dbaec
Electrical
- Apr 9, 2009
- 11
Problem
I have had two 2HP single phase dual voltage motors that trip the overcurrent device on startup. The first motor blew the starting capacitor.
History
These are on a hood exhaust fan on a restaurant. The exhaust fan was installed new 12/08. The fan gets turned on at opening runs about fifteen hours and turned off at closing. In two months the OCD tripped three times. The first two times I was called out to check it out. I reset it, checked startup and run currents, both were normal and all else seemed fine. The third time, under pressure to keep it running, the OCD was bypassed. The thinking was that the OCD was defective. Upon starting the motor the starting capacitor blew. A new motor of the same make and type was sent to replace it. One week later the OCD tripped again.
Technical
The motor is 2HP Dual voltage 115/208-230V.
Connected for 230V.
FLA is 12.7 at 230V.
S.F. is 1.15 at 230V.
Motor has two starting caps, both 295uH.
OCD is set for 125% FLA, ~15.8A.
OCD is three phase (ambient compensated bi-metallic)
(class 10 with single phase sensetivity).
Voltage to motor not running is 246, while running is
243.
Start up current is ~57A decreasing to a stable running
current of 12A in four seconds.
Findings
After double checking the wire connections, fan
direction, belt tension and alignment, I cycled the
motor on and off more than twenty times. During that
time the OCD tripped three times. Each time was within
about five seconds of startup. My ammeter would read
in the high 50s and drop to 12A in about four seconds
then the OCD would trip.
Questions
Is there something my ammeter is not telling me?
Even so, that class 10 OCD should handle ~95A for ten
seconds before tripping. (600%x15.8)
If I'm using the wrong or defective OCD what caused
cap in the first motor to blow?
Any suggestions would be appreciated.
I have had two 2HP single phase dual voltage motors that trip the overcurrent device on startup. The first motor blew the starting capacitor.
History
These are on a hood exhaust fan on a restaurant. The exhaust fan was installed new 12/08. The fan gets turned on at opening runs about fifteen hours and turned off at closing. In two months the OCD tripped three times. The first two times I was called out to check it out. I reset it, checked startup and run currents, both were normal and all else seemed fine. The third time, under pressure to keep it running, the OCD was bypassed. The thinking was that the OCD was defective. Upon starting the motor the starting capacitor blew. A new motor of the same make and type was sent to replace it. One week later the OCD tripped again.
Technical
The motor is 2HP Dual voltage 115/208-230V.
Connected for 230V.
FLA is 12.7 at 230V.
S.F. is 1.15 at 230V.
Motor has two starting caps, both 295uH.
OCD is set for 125% FLA, ~15.8A.
OCD is three phase (ambient compensated bi-metallic)
(class 10 with single phase sensetivity).
Voltage to motor not running is 246, while running is
243.
Start up current is ~57A decreasing to a stable running
current of 12A in four seconds.
Findings
After double checking the wire connections, fan
direction, belt tension and alignment, I cycled the
motor on and off more than twenty times. During that
time the OCD tripped three times. Each time was within
about five seconds of startup. My ammeter would read
in the high 50s and drop to 12A in about four seconds
then the OCD would trip.
Questions
Is there something my ammeter is not telling me?
Even so, that class 10 OCD should handle ~95A for ten
seconds before tripping. (600%x15.8)
If I'm using the wrong or defective OCD what caused
cap in the first motor to blow?
Any suggestions would be appreciated.