katwalatapan
Electrical
- Aug 9, 2011
- 153
Hello,
The existing motor is 3-phase, 208V, 3.82A FLA. It is controlled via an Eaton motor starter rated for 18A and an overload setting of 4.56A. The motor is damaged and as a stop gap measure, an available 1-phase, 208V, 5.68A FLA motor could be installed. I've confirmed with the manufacturer that the exisiting motor starter and overload could be re-used for 1-phase motor, however the max setting of the existing motor overload is 5.23A.
Could the existing motor starter and overload be re-used for this application. I understand, that the max. overload setting should be 125% of the motor FLA, but in this case the max. overload setting is less than the motor FLA. To avoid any starting or overload issues, would it be best to install a new motor starter and overload with higher amperage setting? OR could the existing overload max. setting be acceptable?
I'd appreciate your comments on the above.
Thank you.
The existing motor is 3-phase, 208V, 3.82A FLA. It is controlled via an Eaton motor starter rated for 18A and an overload setting of 4.56A. The motor is damaged and as a stop gap measure, an available 1-phase, 208V, 5.68A FLA motor could be installed. I've confirmed with the manufacturer that the exisiting motor starter and overload could be re-used for 1-phase motor, however the max setting of the existing motor overload is 5.23A.
Could the existing motor starter and overload be re-used for this application. I understand, that the max. overload setting should be 125% of the motor FLA, but in this case the max. overload setting is less than the motor FLA. To avoid any starting or overload issues, would it be best to install a new motor starter and overload with higher amperage setting? OR could the existing overload max. setting be acceptable?
I'd appreciate your comments on the above.
Thank you.