Ok guys, little rusty over here..project management too long and not enough engineering in my life I guess.
We recently surveyed at Pump 150 H.P. 480V 3P. Initial Current was 175A @ .79PF We have a guy who claims he makes a "little black box" that will change the intial PF to .96 reducing the amperage to 144A. I'm assuming this little black box simply has a capacitor in it to counter the inductive load by magnetizing the coils in the motor. Anywho, i'm just working what little info I have to try and figure the reactive power. And what capacitance will bring the reactive power close to 0 leaving almost a totally resistive load. Just for fun. This guy claims his "little black box" will reduce power losses in motors 10-200 H.P. by 6-12%. I'm going to install a Dranetz PX5 before and after this box is installed to see if this will work.
I figure the from what we monitored (175A @ 480 3P)
Your Real or True Power (P) would be (175*480*1.73*.79)/(1000) = 114.8kW
Angle = cos^-1 (.79) = 37.8 Deg.
From this your Apparent power (S) would be the following: 114.8kW / (cos 37.8) = 145kVA
And your Reactive Power (Q) would be 114.8kW(tan 37.8) = 89kVARs
First off, am I right so far?
We recently surveyed at Pump 150 H.P. 480V 3P. Initial Current was 175A @ .79PF We have a guy who claims he makes a "little black box" that will change the intial PF to .96 reducing the amperage to 144A. I'm assuming this little black box simply has a capacitor in it to counter the inductive load by magnetizing the coils in the motor. Anywho, i'm just working what little info I have to try and figure the reactive power. And what capacitance will bring the reactive power close to 0 leaving almost a totally resistive load. Just for fun. This guy claims his "little black box" will reduce power losses in motors 10-200 H.P. by 6-12%. I'm going to install a Dranetz PX5 before and after this box is installed to see if this will work.
I figure the from what we monitored (175A @ 480 3P)
Your Real or True Power (P) would be (175*480*1.73*.79)/(1000) = 114.8kW
Angle = cos^-1 (.79) = 37.8 Deg.
From this your Apparent power (S) would be the following: 114.8kW / (cos 37.8) = 145kVA
And your Reactive Power (Q) would be 114.8kW(tan 37.8) = 89kVARs
First off, am I right so far?