nightfox1925
One of the projects I am looking on involves some 3.3kV motor starters involving Fuse-Contactor motor starter arrangement. Multi-function Motor protection relays (MPR) are also installed in these starters connected to phase and zero-sequence CTs. I observed on our contractor drawings that all the protection elements including the 50/51, 50G element of the MPR are set to open the contactor.
Is this a good design since I always been eyeing on using the 50/51, 50G to trip a breaker and not a contactor? The 415Vac system is solidly grounded and hence the contactor might not be rated to trip on a phase or ground fault.
Further, all there are 415Vac MCP+Contactor starters with MPR relays and are wired in the same manner. I am proposing that the 50/51 and 50G wired to directly trip the MCP via shunt trip and not the contactor.