I have SEL-710 application and we're using stator/rotor/ambient RTD settings. We have enabled TRIP points for these RTD's per motor manufacturer data sheet.
Is it still necessary to include time between starts & starts per hour lockout protection since the RTD's protect the motor against over temperature damage? We were basing these settings on NEMA MG-1 recommendations, 20 min and 3 starts per hour. I'm thinking these settings are not necessary with RTD protection?
We would prefer to remove the previous lockout settings because the 710 outputs to control relay that have seal-in contact and it causes operator have to manually reset the MV starter. The starter scheme has other contacts and is not easy to rewire.
Thoughts?
Is it still necessary to include time between starts & starts per hour lockout protection since the RTD's protect the motor against over temperature damage? We were basing these settings on NEMA MG-1 recommendations, 20 min and 3 starts per hour. I'm thinking these settings are not necessary with RTD protection?