Hi all. I have been working with a softstarter fault issue on my company's equipment for over a month now. The softstart is an Allen-Bradley SMC-3, and the fault is four-flash Phase-Loss/Open Load. I have initiated one fix so far, which initially reduced the faults entirely. What I suspected initially was that the signal from the reverser [5MREV] control block, which ran to both the contactor [5M] coil and the sfst START signal, caused the sfst to finish its prechecks in some machines/instances before the contactor had fully closed, thus faulting a Phase Loss/Open Load. I put the signals and power up on a scope on a non-faulting piece of equipment in my shop and proved this was possible. It took 5M 68ms to close, and A-B specs say the initial checks are done in ~31ms. IDK why this wouldn't happen every time.
The first solution I implemented was then to wire the sfst START signal through the AUX contact of 5M. This delayed the sfst START signal by ~69ms. I changed wiring on 13 machines in two facilities, and all the faults went away -- at least initially. One facility has since reported two of the same faults again in one month's time. This machine used to fault 3-5 times per day before the fix.
I have attached drawings. Sheet 7 is the Power circuit, Sheet 13 is the Control circuit, Rev A before my fix and Rev B after.
My next step is to change out the contactor and reverser and to set up the scope on the troubled machine. I think I need to go back with more than this. What do you all think?
The first solution I implemented was then to wire the sfst START signal through the AUX contact of 5M. This delayed the sfst START signal by ~69ms. I changed wiring on 13 machines in two facilities, and all the faults went away -- at least initially. One facility has since reported two of the same faults again in one month's time. This machine used to fault 3-5 times per day before the fix.
I have attached drawings. Sheet 7 is the Power circuit, Sheet 13 is the Control circuit, Rev A before my fix and Rev B after.
My next step is to change out the contactor and reverser and to set up the scope on the troubled machine. I think I need to go back with more than this. What do you all think?