I am sizing a gas genset to start a 600V 45kW motor driving a centrifugal pump. Motor characteristics are as follows:
Starting Current: 405A
Rated Current: 54A
Total Moment of Inertia: 0.42 kgm2
Speed: 1775rpm
Load at pump operating point: 32kW
Motor starting power is the limiting factor for the genset in this application. My genset sizing software assumes a starting power factor of 0.36 and a running load (input) of 51.7kW, giving a starting load of 87.3kW. This assumes a "low inertia" load and NEMA Code H motor.
Is a starting power factor of 0.36 and starting load of 87.3kW reasonable for this application? I've heard that the rule of thumb for induction motors is a starting power factor of 0.2 (which would give a starting current lower than the running current in this case).
I may be over-analyzing things here but I would really like to know the relationship between starting power, starting power factor, and load characteristics.
Starting Current: 405A
Rated Current: 54A
Total Moment of Inertia: 0.42 kgm2
Speed: 1775rpm
Load at pump operating point: 32kW
Motor starting power is the limiting factor for the genset in this application. My genset sizing software assumes a starting power factor of 0.36 and a running load (input) of 51.7kW, giving a starting load of 87.3kW. This assumes a "low inertia" load and NEMA Code H motor.
Is a starting power factor of 0.36 and starting load of 87.3kW reasonable for this application? I've heard that the rule of thumb for induction motors is a starting power factor of 0.2 (which would give a starting current lower than the running current in this case).
I may be over-analyzing things here but I would really like to know the relationship between starting power, starting power factor, and load characteristics.