rockman7892
- Apr 7, 2008
- 1,176
I work with a client that has a sorting facility that has multiple conveyors/sorters that operate on a 208V system. There are several of these conveyors located throughout the facility with groups of 2-3 conveyors served from a local 480-208/120V step down transformer and secondary 208V panelboards having branch circuits going out to each conveyor.
The conveyors have 208V motors which are started across the line and are started frequently throughout the day. I'm not sure of the exact HP but am told that the full load of each of these conveyors are 102A at 208V.
The client has stated that they experience voltage drop issues when starting these motors frequently thoughout the day resulting in issues with getting motors started and heating of cables.
As a solution to this voltage drop issue they are suggesting increasing the sizes of the step-down transformers mentioned above sizing the transformers to 20% more than required for steady state load to help with voltage issues (The customer is changing all these transformers anyway to re-configured layout of conveyors).
As an example a group of (2) conveyors is currenly fed from a 75kVA transformer. They are suggesting increasing this transformer to 150kVA based on the following...…37kVA per conveyors *2 Conveyors *120% = 89kVA. Next size up is 112kV however 150kVA is being selected.
Is increasing transformer capacity in this manner and effective solution to minimizing voltage drop issues with motor starting? Perhaps a more effective solution may be to provide some means of soft starting motors but client does not seem interested in exploring this option. Would it be more effective to have large step down transformer to group all 208V loads from a common switchboard?