evan63
Electrical
- Jul 29, 2007
- 10
We had a ground fault indicator light come on in one of our substaions recently.After troubleshooting we found out that a 480v 3phase motor was wired wrong,OOPS!One of the phase wires was terminated to ground at the motor and the EGC was hooked up to one of the t-leads of the motor.My question is how did the motor run without any tripping or problems.