Dave Descoteaux
Electrical
- Apr 7, 2017
- 4
Hello,
Our Sag mill motor is rated 1500HP with 4000V, 212A and 0.8 lead power factor, insulation class F and permissible temperature rise 80K. Our motor is actually used at 112% of nominal charge (1320kW, 0.943 lead P.F., 190A, 4220V). We want to know if we can still increase the load without damaging the motor or if the motor capacity is already reached.
In my mind, as it is a synchronous motor, I can go up to 125% of nominal load by adjusting P.F. to 1.0 instead of 0.8 lead. So 4000*212*1.73*1 = 1468kW.
Rated Input power is 4000*212*1.73*0.8 = 1175 kW
1468/1175 = 125% of rated load.
We could also continue overexciting the motor and maybe reach a little more if the temperature limits are respected…
But I want to be sure that we respect the allowable maximal temperature of the motor.
So if I look at the RTDs, what values should I setup my alarms and trip to avoid damaging the motor ? Is it based on actual ambient temperature + permissible temperature rise (80K), or is it based on motor class insulation maximal temperature (155°C for class F)
Ambient temperature of the mill is 20°C and not 40°C. Insulation class is F (155°C) and permissible temperature rise is 80K.
Does the critical temperature to avoid is 155°C – 10°C (hot spot) = 145°C since it is a class F insulation motor? Or does the critical temperature to avoid is 20°C + 80K = 100°C. So that over 100°C temperature rise within the motor will exceed 80K..
There is a huge difference between both so I really need to understand the way it works to adequatly protect the motor.
Do I have to prevent exceeding the 80K temperature rise within the motor whatever ambient temperature is (below 40°C..because I know there are factors to consider if I'm over 40°C ambient) or do I have to prevent exceeding the maximal allowable temperature based on motor class insulation, or both .. ??
Thanks !
Dave
Our Sag mill motor is rated 1500HP with 4000V, 212A and 0.8 lead power factor, insulation class F and permissible temperature rise 80K. Our motor is actually used at 112% of nominal charge (1320kW, 0.943 lead P.F., 190A, 4220V). We want to know if we can still increase the load without damaging the motor or if the motor capacity is already reached.
In my mind, as it is a synchronous motor, I can go up to 125% of nominal load by adjusting P.F. to 1.0 instead of 0.8 lead. So 4000*212*1.73*1 = 1468kW.
Rated Input power is 4000*212*1.73*0.8 = 1175 kW
1468/1175 = 125% of rated load.
We could also continue overexciting the motor and maybe reach a little more if the temperature limits are respected…
But I want to be sure that we respect the allowable maximal temperature of the motor.
So if I look at the RTDs, what values should I setup my alarms and trip to avoid damaging the motor ? Is it based on actual ambient temperature + permissible temperature rise (80K), or is it based on motor class insulation maximal temperature (155°C for class F)
Ambient temperature of the mill is 20°C and not 40°C. Insulation class is F (155°C) and permissible temperature rise is 80K.
Does the critical temperature to avoid is 155°C – 10°C (hot spot) = 145°C since it is a class F insulation motor? Or does the critical temperature to avoid is 20°C + 80K = 100°C. So that over 100°C temperature rise within the motor will exceed 80K..
There is a huge difference between both so I really need to understand the way it works to adequatly protect the motor.
Do I have to prevent exceeding the 80K temperature rise within the motor whatever ambient temperature is (below 40°C..because I know there are factors to consider if I'm over 40°C ambient) or do I have to prevent exceeding the maximal allowable temperature based on motor class insulation, or both .. ??
Thanks !
Dave