KRISHNA746
Electrical
- Sep 30, 2023
- 1
One of our substations has a 6.6kV switchboard with two incomer(NC) and bus coupler(NO) scheme, this board further feeds motor loads.
During starting of one of the motor P1 515kW FLC-56() ,it so happened that motor tripped on over current protection(450A 0sec) and corresponding incomer of that section tripped on feeder differential protection.
On further checking it was observed that b phase of incomer failed. However motor was healthy.
I would be grateful if i could get clarifications on following points from community.
1.During failure it was observed from bus PT and line PT that there was voltage dip in Y and B phases, however there was not fault in Y phase of incomer.
2.Motor P1 relay (Schneider P141) recorded current of around 3kA in Y and B phase, however motor was healthy.
During starting of one of the motor P1 515kW FLC-56() ,it so happened that motor tripped on over current protection(450A 0sec) and corresponding incomer of that section tripped on feeder differential protection.
On further checking it was observed that b phase of incomer failed. However motor was healthy.
I would be grateful if i could get clarifications on following points from community.
1.During failure it was observed from bus PT and line PT that there was voltage dip in Y and B phases, however there was not fault in Y phase of incomer.
2.Motor P1 relay (Schneider P141) recorded current of around 3kA in Y and B phase, however motor was healthy.