Thank you all for the input. We've been working on this problem again today. First of all just to answer some of your questions, the motor is a DOL start, the current unbalance relay is set at 3Amps there is no time delay on the relay it is instantaneous and this is applicable to all three motors, like I said the other 2 are working perfectly. As for my last statement I would repeat," We've done couple of tests and from the analysis it is evident that the phase unbalance only happen during motor startup, within 100milliseconds period, from then on the phases goes back to 120 deg. Today we were busy testing the cable (just so you know this is at a nuclear power plant) we’ve got switchgear room situated at the electrical building which is at 7 meter level. The motor is in the turbine hall –6 meter level, and there are two 150mm^2 cable thickness and about 120meters long (for conversions 1m = 3.28ft = 39,4in). The test on the cable shows there is 11% difference on impedance but it was ruled out as the cause of trip because the acceptable standard is 10% for new cable. So, we tightened some connection that we suspected and cleaned them and even swoped the contactor again, then we tested to motor. Three times in the row the motor did not trip, just before we finalize the findings we decided to run it another three time… guess what, three times in the row it tripped. We looked at the results again and it shows that for few milliseconds during startup red and white phases are 180 degrees apart. What could be the cause of this???? What will shift the angle for few seconds????