I'm having issues with an Allen bradley voltage relay that is used on a 88Hp pump motor. The model of the relay is 813S-V3-690V. The motor runs at 600V.

The relay "AL" led keeps flashing from red to green really quickly. I've been looking over the internet to find a user manual of some sort that would help me understand what causes the AL led to go crazy.. no cigar.

Any help is more than welcomed !

Thanks
Pat
 
Replies continue below

Recommended for you

I would guess that "AL" may be 'Alarm'. It could be a self alarm, indicating a failure of the device.

I would check with Rockwell Automation (Parent Co) for manaual details.

Other things you can try. Measure with a separate meter the input voltage to the relay - is it within reasonable (Vnom*.9) range? If you can, remove the control power, wait a minute and reapply the control power and observe operation. Try removing all sensing voltage and see if the device operates as designed. All of the above assume you are using proper safety practices and can accept a trip operation of the protected motor.


 
The led flashing means it is doing it's job, it is detecting that the voltage is outside of the settings you have made.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> faq731-376
 
Thanks for the replies guys,

Went and mesured the voltage, it had the wanted 600V L-L.

Now, it was recently changed, so maybe the dip switches aren't set properly. Using the pdf that smallgeek gave me, i will try and see if they're correctly set.

Thanks again
 
I would guess that they have switches 3/4 set for 690 volts. That would make them blink.
 
Here are the dip SW settings
1:OFF
2:OFF
3:ON
4:ON
5:OFF
6:ON

I'm not sure i understand all of the SW settings.

For Sw1: SW1 selects the power-ON delay (inhibit of alarm at the power-ON): 1s or 6s.
Does this means the delay before the relay trips ?

SW3-4 are set for 600V ph-ph. this should be ok.

Is there a reset on the relay ? maybe it tripped for a reason that isnt there anymore ?

I'm creating a imageshack account to post some pictures too.

Thanks
Lespoils

 
Or you could read the manual, which clearly states that rapid bicolour LED flashing indicates "phase sequence is wrong or one phase is lost".

SW1 selects the power-ON delay (inhibit of alarm at the power-ON): 1s or 6s. Does this means the delay before the relay trips ?

No, it means the relay will not alarm for 1 or 6 seconds when power is first applied. The trip delay is set by the setpoint dials on the front.

Is there a reset on the relay ?

Again, as the manual states, no. The trip conditions only persist while ever the voltage levels are outside the setpoints.
 