MakingAComeback
Electrical
- Aug 22, 2005
- 23
Folks,
We started for the first time recently an 18000 hp induction motor: 13.8kV, 900 rpm. The Multilin 469 relay took it out immediately on short circuit. In round numbers phase C current was about 8000 amps, while phases A and B currents were the same at 4500 amps or so. Normal starting current is less than 3000 amps. We spent a lot of time checking the current transformer circuity and concluded that the problem wasn't there. After much head scratching and a surge test of the stator we concluded that the T3 and T6 leads had been marked wrong at the factory. Reversed them and all was well on the next start.
Conceptually I can grasp what caused the symptoms we observed, but it would be educational to see a mathematical expression that represents our situation. Can you help?
We started for the first time recently an 18000 hp induction motor: 13.8kV, 900 rpm. The Multilin 469 relay took it out immediately on short circuit. In round numbers phase C current was about 8000 amps, while phases A and B currents were the same at 4500 amps or so. Normal starting current is less than 3000 amps. We spent a lot of time checking the current transformer circuity and concluded that the problem wasn't there. After much head scratching and a surge test of the stator we concluded that the T3 and T6 leads had been marked wrong at the factory. Reversed them and all was well on the next start.
Conceptually I can grasp what caused the symptoms we observed, but it would be educational to see a mathematical expression that represents our situation. Can you help?