No reference to provide. We just designed the fix and built it.
The first thing we did was assume that the safety factor was unity (we had signs of failure). We then calculated what supplemental buttress would be needed (on a unit foot basis) to increase the safety factor to 1.5 (understanding the mode of failure and the concern on global, internal and external failures). We then considered the spacing of the pilaster (i.e., 8 ft) and determined the lateral load that would act on the pilaster. At that point it's a structural beam that's vertical, if you get my point. You have to consider bending moments, point reactions (i.e., at the tieback) and structual reinforcement. Each pilaster has a footing to support the weight of the pilaster and also the vertical contribution from the battered tie-back.
We used cast-in-place construction. We ruled out pre-cast construction as the intimate contact between the pilaster and the wall would still require some grouting or such.