yellerwhale
Structural
- Dec 9, 2009
- 4
We've got a two story building under construction that was designed under the 2001 CBC. We specified Simpson BP-58 (2"x2") plate washers on each shear wall anchor bolt. The permit was issued under the 2007 CBC, but we and the plan checkers didn't catch one Code upgrade -that the 2007 Code specifies 3"x3" plate washers on shear wall anchor bolts. Of course, rather than check for conformance with the approved documents, now the inspector wants the washers changed to 3"x3". Any Ideas?? I'm considering proposing only changing the washers on shear walls stressed over 2/3 their design capacity.