How do you handle partition loading in multi-family residential?
I could see a few cases:
1. Treat it as a dead load - typically 10psf is what I see. This load would not get reduced as it might for a live load. Most likely this load will be there.

2. Treat it as a live load - 15 psf as noted in ASCE 7. This is typically done in office buildings but because the code says "where partitions will be erected or rearranged" I suppose this could apply to multifamily residential as well.

3. Some combination of the above.

I could see an argument made either way. I mean typically the walls of multi-family residential are not going to move, but they could, just not as regularly as say, an office building.

Thanks!

EIT
 
Replies continue below

Recommended for you

1.



Check out Eng-Tips Forum's Policies here:
faq731-376
 
I have never worried about it except typically to add a double joist under it if it is of significant length. Let's face it, an interior wall is only 2x4's and 2 layers of sheetrock - so about 6 psf. That gets lost in the noise in the grand scheme of things. I never max out spans in any structure to prevent serviceability complaints so there is always plenty of fat.
 
I've been using:

-actual weight for demising and corridor walls which usually don't load horizontal framing anyhow.
-5 psf extra on the floor area based on some typical unit plans.

This is something that I wish the codes covered explicitly. Many of my competitors just assume that it's covered in the live load.



I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Treat as a dead load at the location it is to be installed. Never seen the moveable partition load applied in residential.
 
I guess I should clarify my post. 6 PSF x 9' height = 54 PLF. The way I look at it, the wall takes up about 6" of floor space with baseboard. - so you could subtract 20 plf of potential live load. Still does not make up for it completely , but close enough in my book. I def. take it into account for seismic, however.
 
If it's condos, I include the partition load. If it's apartments or dorms, I include it as a dead load. I include the mass of the partitions for seismic regardless. After some debate with other engineers in my office, I agree with XR250 that it washes out with the conservatism of the other loads.
 
@mike: why the different treatment for condos.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
It's very unlikely that an apartment unit will have the wall configurations changed unless it's a building wide renovation, but individual owners of condos may be able to make renovations. We started doing that when we had a high end condo project where the architect specifically told us partitions won't be erected until they are sold.
 