patibar
Chemical
- Sep 30, 2012
- 26
In Our site there are total seven plants and Sea water is supplied to some of the plants. The first plant near to the sea water supply having issues in return line. Because of high pressure drop available, we have inserted a multi hole orifice in the return line (72"). Then we found flashing of water at the exit of return line like a heavy jet. Then we have inserted one more multi hole orifice at the end and distributed the available pressure drop (~3.5 Kg/cm²).
Now the problem of choking is happening frequently. Pipe is FRP pipe and we found in the last shutdown the pipe inner wall liner got removed and strucked in holes of orifice along with sea shells. We have made a temporary bypass (24" line with one more multi hole orifice) across the second orifice, through which we have got some improved flow.
Data
required flow is 14500 m³/h
Existing Pipe Line is 72"
Two multi hole orifices
First orifice pressure drop 1.5 Kg/cm²
Second Orifice Pressure drop is 1.7 Kg/cm²
My question is why a multi hole orifice is required? Why vibrations in Pipeline happens, when we insert a single hole orifice. Can we insert a single multi hole orifice instead of two?
Is there any special sizing calculations required for Sea Water Lines. I have read that for gravity lines, we may need to follow Froude number < 0.3. Her Sea Water supply is coming from a pumping station and then it passes through series of filters and exchangers and finally returned to sea through return line.
Thanks
Rajesh
Now the problem of choking is happening frequently. Pipe is FRP pipe and we found in the last shutdown the pipe inner wall liner got removed and strucked in holes of orifice along with sea shells. We have made a temporary bypass (24" line with one more multi hole orifice) across the second orifice, through which we have got some improved flow.
Data
required flow is 14500 m³/h
Existing Pipe Line is 72"
Two multi hole orifices
First orifice pressure drop 1.5 Kg/cm²
Second Orifice Pressure drop is 1.7 Kg/cm²
My question is why a multi hole orifice is required? Why vibrations in Pipeline happens, when we insert a single hole orifice. Can we insert a single multi hole orifice instead of two?
Is there any special sizing calculations required for Sea Water Lines. I have read that for gravity lines, we may need to follow Froude number < 0.3. Her Sea Water supply is coming from a pumping station and then it passes through series of filters and exchangers and finally returned to sea through return line.
Thanks
Rajesh