I was asked to look at a 12 story concrete frame condo bldg with brick veneer- called for relief angles at every floor, anchored to slab edge. Finding out that the vert leg of the angle is as much as 3" away from concrete edge! And the brick is up right against the bottom of relief angle!
The 5/8" bolts at 24" oc cannot support brick with that eccentricity. The brick should support itself on the concrete ledge below- 40 pdf x 120' = 4800 plf or 100 psi - low.
Then with brick supporting itself and free to move upward, need to support laterally. The metal stud wall ties may or not be connected properly. Thinking of vertically slotting the angle holes to allow the angle to move vertically. The bolts would only provide lateral support.
What do you guys think?
The 5/8" bolts at 24" oc cannot support brick with that eccentricity. The brick should support itself on the concrete ledge below- 40 pdf x 120' = 4800 plf or 100 psi - low.
Then with brick supporting itself and free to move upward, need to support laterally. The metal stud wall ties may or not be connected properly. Thinking of vertically slotting the angle holes to allow the angle to move vertically. The bolts would only provide lateral support.
What do you guys think?