Multiple Cooling Towers equalizer piping

Status
Not open for further replies.

capaula

Mechanical
Oct 23, 2008
19
What is the correct way to size an equalizer pipe for 5 cooling towers working in parallel?
I am not able to find this anywhere.
Thanks
 
Replies continue below

Recommended for you

Check with BAC or Bell and Gossett's "Cooling Tower Pumping and Piping" tech manual.
 
What kind of tolerance are you looking for equal flows?

Effectively you will be trying to equalize the pressure in each of the branches. If you have a fixed flow you can introduce orifices to reduce flow in the higher flow branches. If it is more variable you may want to explore using a flow control valve and a flow meter on each branch.
 
The bigger the better. Running towers in parallel will prevent problems with shrink and swell with starting and stopping of condenser water pumps. Keep velocity below 3 fps, max conditions. It's not like piping that gets distributed throughout a building; you might be talking about a 30' run. Go for the 14" vs. the 10" (as an example) to avoid problems.
 
Just to clarify, is this equalizer connecting sumps together or supply lines? If sumps, the "bigger is better" theory is definitely the way to go.
 
You can use GESTRA sizing of header in a specific pipe branches
 