Is it possible to serve several DX coils using one air-cooled condenser and if possible, what is the control strategy that I should use? Also, is there reference material (abstracts, etc) that I could access to help me with this problem?

Thanks for you help,
M.Humes
 
Replies continue below

Recommended for you

Yes, it can be done. You need to speak to a manufacturer for details of the correct product. Toshiba or Mitsubishi make such systems, they are commonly called multi-splits.

Hope this helps.

Cooky
 
Connecting multiple DX coils to a single condensing unit is done frequently, and to both air conditioning and refrigeration systems. Refrigeration systems with multiple evaporators will normally employ eprs (evaporator pressure regulators) when it is desired to operate the coils at different temperatures.

But there are many ways to control a multiple evaporator systems. You will need to be more specific about your application for me to suggest a control scheme.
 
HI Friends,

First, sorry about my poor english.
Cooky is correct as usual. As a HITACHI application engineer in Brasil, I must include HITACHI SET FREE System in the wall. see the site:
For a very simple explanation, the condenser unit works with INVERTER DRIVEN scroll compressor, that controls the service frequency, so, quantity of refrigerant that goes up to the coils (evaporators). Every coil has an electronic expansion valve (EXV), in time, controls (PID) individually each coil cooling/heating capacity by a temperature set/measure of each zone.

Stay Cool...
 