We have a 11 kV bus bar with about 14 MVA of loads (90% motors).
We got (customer data) the short circuit current values: 35 kA as Ikss (subtrans I)
I feel such value a bit too high. Also considering the motor contribution I was expecting 12-13 kA.
(assuming a 15 MVA 9% trafo feeding the system we get 8.75 kA at 11 kA + about 3600A as motor contribution (sum of their starting currents))
What's your experience?
I have the impression that we could get 35 KA only if directly connected to a bus with the generators (we don't know how "our" 11Kv bus is connected)
Thanks in advance for any feedback