In North America:
Motor voltages are multiples of 115 Volts,
System voltages are multiples of 120 Volts.
In the dim past, the multiple of 115 Volts was 2300 Volts.
The corresponding multiple of 120 Volts was 2400 Volts.
In the 40s and 50s, many 2400 Volt delta systems were upgraded to star systems.
The system voltages became 4156.9 Volts, rounded to 4160 Volts.
The 2300 Volts delta motors became 3983.7 Volts, rounded to 4000 Volts.
It is common and accepted practice to connect 4000 Volt rated motors to 4160 Volt systems in North America.
By the way, your full load Amps is 160 Amps.
I hope that your O/C settings reflect that current.
Nothing new here!
Have you checked your incoming voltage?
A possible cause may have been an upstream voltage regulator.
Depending on the stiffness of your supply system, the utility may have voltage regulators upstream, or On-Load-Tap-Changers on the supply transformer at the substation, possibly both.
If the 1250 HP motor is causing line voltage drops, the voltage regulators and tap changers will be ramping up the supply voltage to compensate for the line drops.
If the nature of the overload was such that it took some seconds to trip, then the voltage regulators and tap changers may have time to go up one more tap, possibly making the situation worse.
When the motor did trip, the reduced line current would result in less voltage drop in the distribution circuit.
This could easily cause an over-voltage trip, after the motor tripped off-line.
An over-voltage relay will often be energized when the motor is not, so as to prevent start attempts in the event that the voltage is too high.
You may consider inhibiting an over-voltage trip in the event of an over-load trip.
But I could be wrong.
Bill
--------------------