- Jan 18, 2009
- 18
Hi everyone,
We will install solid state soft starter to drive 2MW 6KV motors. The soft starter will fed by 13.8kV switchgear via 13.8/6kV captive transformers.
The solid state reduced voltage starter switches on-off during starting and causes harmonic component in the network. I know VFD generally needs input/output filter to limit THD. However, I do not find any filter equipped in the catalogue of soft starter manufacturer.
I wonder how we can control input/output THD of soft starter? If we do not limit THD, shall the captive transformer be designed specially to withstands harmonics ?
Thanks,
Parkpower
We will install solid state soft starter to drive 2MW 6KV motors. The soft starter will fed by 13.8kV switchgear via 13.8/6kV captive transformers.
The solid state reduced voltage starter switches on-off during starting and causes harmonic component in the network. I know VFD generally needs input/output filter to limit THD. However, I do not find any filter equipped in the catalogue of soft starter manufacturer.
I wonder how we can control input/output THD of soft starter? If we do not limit THD, shall the captive transformer be designed specially to withstands harmonics ?
Thanks,
Parkpower