We've been involved in a lot of replacements of Unit substations recently that involve the replacement of MV Switch, Transformer and LV SWGR/SWBD with new equipment.
With these replacements the obvious economical solution is to provide a MV switch on the primary but with consideration for Arc Flash it may make better sense technically to provide a Breaker (metal enclosed) or a VFI pad mount type transformer both of which have CT's on transformer secondary for AF mitigation purposes. Obviously these solutions for mitigating AF come with an increased cost and was curious to hear the experience of others for providing such solutions considering economics?
With LV SWGR an MM switch can be installed on the main breaker which will mitigate AF on secondary of main but will still leave the line side of the main exposed for AF. This may or may not be a concern based on operating procedures (always opening primary switch first before close/rack breaker) however if it is a concern mitigation on the primary is the only solution. With a SWBD in most cases because of the open construction of the SWBD the MM on the main breaker cannot provide AF mitigation benefit for entire board so mitigation on the primary is necessary.
I appreciate any experiences or insight others have with consideration for cost and situations where the customer may not be aware of potential hazards.
With these replacements the obvious economical solution is to provide a MV switch on the primary but with consideration for Arc Flash it may make better sense technically to provide a Breaker (metal enclosed) or a VFI pad mount type transformer both of which have CT's on transformer secondary for AF mitigation purposes. Obviously these solutions for mitigating AF come with an increased cost and was curious to hear the experience of others for providing such solutions considering economics?
With LV SWGR an MM switch can be installed on the main breaker which will mitigate AF on secondary of main but will still leave the line side of the main exposed for AF. This may or may not be a concern based on operating procedures (always opening primary switch first before close/rack breaker) however if it is a concern mitigation on the primary is the only solution. With a SWBD in most cases because of the open construction of the SWBD the MM on the main breaker cannot provide AF mitigation benefit for entire board so mitigation on the primary is necessary.
I appreciate any experiences or insight others have with consideration for cost and situations where the customer may not be aware of potential hazards.