I am reviewing an application where a 4.16kV MV VFD is being fed from an upstream MV MCC through a fused contactor. The contactor has a multilin 735 relay on the feeder to the VFD. It also appears that a multilin 469 relay will be located at the VFD enclosure for providing motor protection in addition to the protection that the drive provides. The VFD can be bypassed when needed to operate the motor (300hp) across the line thus a need for a separate motor protection relay. The drawings currently show the 469 CT's located on the drive primary however I believe they should be located on the load side of the VFD in order to "see" the motors current thermal state when operating on the VFD (based on when I read in another post on the forum)
My question relates to the protection settings on the 735 relay in this application. In terms of setting the pickup level is it similar to primary protection on a LV drive where the pickup level should be set at 125% of drive input rating. Drive input rating in this case is 70A so I'm thinking a pickup of around 90A or so should be adequate.
-Would an Instantaneous pickup be recommended for this application? I saw in another thread that it was recommended to set the Instantaneous setting above the
secondary fault current from the drive? Is there a reason for this or good way of estimating this fault current if it is not stated in the drive information?
-In terms of setting the feeder relay time delay are there any special considerations other than coordination with upstream protection and the downstream 469
relay? The VFD appears to have an internal 600kVA transformer so I don't know if any consideration needs to be given for protection of it related to through-
faults, etc..
-I'm assuming that 469 relay is set as you typically would for an across the line motor application. Are there any special considerations related to the pickup,
OL curve, and INST settings that need to be considered?
- Both the 735 and 469 relays both trip the upstream MV fused contactor. Are there any special considerations in terms of coordination since they all trip same
device? Any special considerations with the fuse?
My question relates to the protection settings on the 735 relay in this application. In terms of setting the pickup level is it similar to primary protection on a LV drive where the pickup level should be set at 125% of drive input rating. Drive input rating in this case is 70A so I'm thinking a pickup of around 90A or so should be adequate.
-Would an Instantaneous pickup be recommended for this application? I saw in another thread that it was recommended to set the Instantaneous setting above the
secondary fault current from the drive? Is there a reason for this or good way of estimating this fault current if it is not stated in the drive information?
-In terms of setting the feeder relay time delay are there any special considerations other than coordination with upstream protection and the downstream 469
relay? The VFD appears to have an internal 600kVA transformer so I don't know if any consideration needs to be given for protection of it related to through-
faults, etc..
-I'm assuming that 469 relay is set as you typically would for an across the line motor application. Are there any special considerations related to the pickup,
OL curve, and INST settings that need to be considered?
- Both the 735 and 469 relays both trip the upstream MV fused contactor. Are there any special considerations in terms of coordination since they all trip same
device? Any special considerations with the fuse?