A new facility will include 5 - 600 hp motors, along with roughly 200 KVA of 480 VAC load. It would seem to be an application requiring MV distribution and motors, but a cost analysis is pointing toward LV (480 VAC) -
- The motors are part of packaged compressor units which are standard with 480 VAC motors and pre-mounted RV starters.
- There is a significant (20%) cost adder to go with MV motors.
- MV motors would require starters to ship "loose", requiring add'l field labor/space. The utility requires RV starters.
- All loads are in close proximity (less than 100') to the proposed switchboard location and service entrance, reducing the conductor/labor costs associated with the LV installation.
- Significant add'l cost to go with the MV switchgear.
Are there other factors I should be considering in the MV-LV decision? Although at first glance it looks like it should be MV, the costs seem to point to a 480 VAC system.