leoliu
Electrical
- Apr 21, 2005
- 34
Hi all,
I couldn't find any references discussing what is the accuracy of MW and Mvar derived from VT and CT in substations. Supposing both VT and CT have 1% ratio error and have 0.5 degree (30 minutes) phase error, how much error do you think MW and Mvar will be? I am talking about 115kV or 345kV transmission line flow metering.
My theory is that
delta(P)/P = 1% + 1% + Q/P * (3.14/180)
delta(Q)/Q = 1% + 1% + P/Q * (3.14/180)
Since P (MW) is normally much larger than Q (Mvar) in transmisions, delta (Q)/Q i.e. the error of Mvar metering will be much larger than the error of MW.
Thanks.
I couldn't find any references discussing what is the accuracy of MW and Mvar derived from VT and CT in substations. Supposing both VT and CT have 1% ratio error and have 0.5 degree (30 minutes) phase error, how much error do you think MW and Mvar will be? I am talking about 115kV or 345kV transmission line flow metering.