We have had 3 small fires at distribution regulating stations, occuring near a control cabinet. The cabinet houses a "motorized regulator". We send a 120VAC signal from our RTU to a small motor, which turns the actuator screw on a Fairchild Model 10 or 64 regulator. The Fairchild regulator controls natural gas loading the main line regulators. This is how the pressure outlet setpoint is manipulated.
We've used this special setup for 30 years, and have never had a problem. Now, these fires occurred in the last 6 months.
We have limit switches on the motor to avoid pressure extremes (they switch power to the motor and are not monitored). The motor and switches are not sealed.
We have noticed excess gas venting at some sites. Others are venting gas thru the adjustment screw, into the cabinet. We believe this is the source. Ignition is probably caused by the arc in the switches.
I'm just wondering if anybody else has experienced this? If so, were you using Fairchild regulators?
How do you control the setpoint of your main distribution station regulators? I know we use an antiquated method, but it works and it's CHEAP!
Any other thoughts or opinions?
We've used this special setup for 30 years, and have never had a problem. Now, these fires occurred in the last 6 months.
We have limit switches on the motor to avoid pressure extremes (they switch power to the motor and are not monitored). The motor and switches are not sealed.
We have noticed excess gas venting at some sites. Others are venting gas thru the adjustment screw, into the cabinet. We believe this is the source. Ignition is probably caused by the arc in the switches.
I'm just wondering if anybody else has experienced this? If so, were you using Fairchild regulators?
How do you control the setpoint of your main distribution station regulators? I know we use an antiquated method, but it works and it's CHEAP!
Any other thoughts or opinions?