'n' on Dyn11 transformers?

Status
Not open for further replies.
Replies continue below

Recommended for you

busbar,

Not necessarily a mistake. If the transformer is a step up transformer, it would be the X0 terminal, and the H0 terminal on a step down transformer.
 
If I remember right, when there is no 'n' in the vector group designation, e.g. Dy11, the neutral is not brought out (not accessible for use). When there is an 'n' in the vector designation the neutral terminal 'n' or 'X0' is available.

Please correct me if I am wrong!

God bless!
 
The "n" stands for the neutral being brought out of the transformer tank and being available for current measurement or for being earthed. If "n" is absent from DYn11 that means it is an isolated neutral Delta-wye Xmer
 