There are a few factors that play into how much of an issue it will be.
Ceiling finish - is it a suspended ceiling (probably not in all rooms of the structure if it is a single family residence) or gyp board applied directly over the bottom chord of the trusses? With gyp board ceilings, large cracks can occur at the ceiling / wall interface due to vertical movement of the bottom chord of the truss. Simpson Strong-Tie (
manufactures a clip (DTC, STC or something like that) that attaches to the bottom chord and provides for vertical deflection. In their catalog, there is also a detail illustrating that the gyp board on the ceiling is not connected directly adjacent to the partition (to allow for the ceiling to slip by the wall). Crown molding can be installed to mask this, if necessary.
Truss spans - how long are the trusses spanning? Shorter span trusses will not have as much movement vertically at the bottom chord as longer span trusses (assuming they are designed and fabricated correctly). Now you may be asking what is considered short and what is considered long? For standard wood trusses for a single family residence, I would consider trusses spanning around 35 to 40 feet or so to be a long span.
One other attachment I've seen is created by providing 2x blocking laid flat attached perpendicular to the truss bottom chords (end nailed through the chord of the truss and each end of the blocking with 16d nails). Then another 16d nail is nailed vertically through the blocking into the top plate of the partition (interior, non-load bearing) walls. A gap of 3/4" or so should be provided between the blocking and the top of the partition wall. This creates a situation where the nails will be loaded in withdrawal so vertical movement can occur a lot more readily than if the nails were toenailed or somehow loaded in shear only. (I've never used this detail but have seen it recommended by some truss designers).
Sometimes the truss calculations (provided by the manufacturer or designer) will have details addressing these issues. If details have not been provided (common), maybe check with the manufacturer / designer and see what they recommend. Also, the calculations usually have the calculated deflection of each of the trusses (handy for determining how much vertical movement you will need to account for).