Dear all,
would appreciate if anyone is willing to help me with following:
I manage to figured out the ventilation calculation for duct/grilles sizing for E.R. inlet (but need to double check, air-in is not the issue).
Calculated following:
1. Airflow for combustion from engines (Value X - m[sup]3[/sup]/s)
2. Airflow for evacuation of heat emission (Engines, pipes, electro cabinets) (Value Y - m[sup]3[/sup]/s)
3. Total airflow required (Value Q - m[sup]3[/sup]/s) / devided by 2 (two ducts)
4. Maximum airflow velocity shall not exceed (v): 6 m/s
5. Duct sizing (minimum): A = Q/v (m[sup]2[/sup])
6. Air Inlet grilles have a pressure drop of following: ∆p = 1,4 x v[sup]2[/sup]
7. Calculation of new flow velocity (∆p, ω, where ξ=2,5 (minor loss coef.); ρ=1,13kg/m3 (air density))- v/ω =1,15
Velocity needs to be increased by 15%; Q[sub](1)[/sub] = Q x 1,15 (m[sup]3[/sup]/s)
8. v[sub](1)[/sub] = Q[sub](1)[/sub]/A = 8 m/s
9. Second iteration: ∆p = 1,4 x v[sub](1)[/sub] ; ω[sub](1)[/sub]
10. Fan in air out requires minimum of free flow rate of Q[sub](1)[/sub] - condition satisfied.
(Air density: 1,13 ; Base temperature: 30 degree celsius; Peak temp: 40 degree celsius;
temp. difference: ∆T =10; Minor loss coef: ξ=2,5; Specific heat capacity of air: c=1,01)
My question is following:
How to calculate minimum Air-OUT ducts and Grilles size, in a way to avoid use of fan pushing air out? (natural outlet of air)?
The ducts/grilles must be sufficient to exhaust this amount of air - without creating a large back pressure issue.
Which formula do I need to use?
In attachment preliminary plan and side views.
Thank you very much all in advance.
would appreciate if anyone is willing to help me with following:
I manage to figured out the ventilation calculation for duct/grilles sizing for E.R. inlet (but need to double check, air-in is not the issue).
Calculated following:
1. Airflow for combustion from engines (Value X - m[sup]3[/sup]/s)
2. Airflow for evacuation of heat emission (Engines, pipes, electro cabinets) (Value Y - m[sup]3[/sup]/s)
3. Total airflow required (Value Q - m[sup]3[/sup]/s) / devided by 2 (two ducts)
4. Maximum airflow velocity shall not exceed (v): 6 m/s
5. Duct sizing (minimum): A = Q/v (m[sup]2[/sup])
6. Air Inlet grilles have a pressure drop of following: ∆p = 1,4 x v[sup]2[/sup]
7. Calculation of new flow velocity (∆p, ω, where ξ=2,5 (minor loss coef.); ρ=1,13kg/m
Velocity needs to be increased by 15%; Q[sub](1)[/sub] = Q x 1,15 (m[sup]3[/sup]/s)
8. v[sub](1)[/sub] = Q[sub](1)[/sub]/A = 8 m/s
9. Second iteration: ∆p = 1,4 x v[sub](1)[/sub] ; ω[sub](1)[/sub]
10. Fan in air out requires minimum of free flow rate of Q[sub](1)[/sub] - condition satisfied.
(Air density: 1,13 ; Base temperature: 30 degree celsius; Peak temp: 40 degree celsius;
temp. difference: ∆T =10; Minor loss coef: ξ=2,5; Specific heat capacity of air: c=1,01)
My question is following:
How to calculate minimum Air-OUT ducts and Grilles size, in a way to avoid use of fan pushing air out? (natural outlet of air)?
The ducts/grilles must be sufficient to exhaust this amount of air - without creating a large back pressure issue.
Which formula do I need to use?
In attachment preliminary plan and side views.
Thank you very much all in advance.