Hello all,
can anybody explain to me how 9.23.6.1 sentence 2c provides any anchorage into a 8" wide foundation wall for a home. We qualify as low wind and low seismic area, however I can't figure out how 2c could be subsituted in place of 2b (1/2" anchor bolts spaced at 2.4m O/C into concrete. Are the sill plates nailed into the side of the concrete through the 2x4 on edge?
I got a 3 storey home, which qualifies as part 9, so alot of the loads are quite small, but were at the cusp of where we could be considered part 4 (were just under the 600m2 outline area)
9.23.6. Anchorage
9.23.6.1. Anchorage of Building Frames
1) Except as required by Sentence 9.23.6.3.(1), building frames shall be anchored to
the foundation unless a structural analysis of wind and earthquake pressures shows
anchorage is not required.
2) Except as provided in Sentences (3) to (6), anchorage shall be provided by
a) embedding the ends of the first floor joists in concrete,
b) fastening the sill plate to the foundation with not less than 12.7 mm diam
anchor bolts spaced not more than 2.4 m o.c., or
c) embedding in concrete two 38 mm by 89 mm sill plates placed on edge and
separated by blocking spaced 1.2 m o.c.
can anybody explain to me how 9.23.6.1 sentence 2c provides any anchorage into a 8" wide foundation wall for a home. We qualify as low wind and low seismic area, however I can't figure out how 2c could be subsituted in place of 2b (1/2" anchor bolts spaced at 2.4m O/C into concrete. Are the sill plates nailed into the side of the concrete through the 2x4 on edge?
I got a 3 storey home, which qualifies as part 9, so alot of the loads are quite small, but were at the cusp of where we could be considered part 4 (were just under the 600m2 outline area)
9.23.6. Anchorage
9.23.6.1. Anchorage of Building Frames
1) Except as required by Sentence 9.23.6.3.(1), building frames shall be anchored to
the foundation unless a structural analysis of wind and earthquake pressures shows
anchorage is not required.
2) Except as provided in Sentences (3) to (6), anchorage shall be provided by
a) embedding the ends of the first floor joists in concrete,
b) fastening the sill plate to the foundation with not less than 12.7 mm diam
anchor bolts spaced not more than 2.4 m o.c., or
c) embedding in concrete two 38 mm by 89 mm sill plates placed on edge and
separated by blocking spaced 1.2 m o.c.