NEC 240.21B - 25 Ft Feeder Tap Rule
power2engineer
53
Do I need to put Breakers for 2 Separate Panel board feeders supplied from load side of Automatic transfer switch with Utility and Stand by generator sources the 2 Panel boards are within 25 Ft from Service entrance ATS (with Stand by generator source) and has their own main breakers as well. Please See attached Sketch
 https://files.engineering.com/getfile.aspx?folder=39c0348f-5973-44c0-ad2f-1c451410444c&file=NEC_240.21_25_FT_TAP_RULE.pdf
This is the provided link.
Keith Cress
kcress -
The breakers upstream of the ABT switch protect the 1200A cables. The 600A tap appears to meet the rules requirements.
[url=https://www.nfpa.org/Assets/files/AboutTheCodes/70/70-A2013-ROPDraft.pdf said:
PROPOSED NFPA 70® 2014 Edition National Electrical Code® 240.21B(2)]
I copies this excerpt from the "final" Draft on NFPA's website.