I am starting to battle it out with an FPE about receptacles
under raised flooring, and the following
appears on the scene. Note figure 1, and the following caviot. "not used for environmental air". Plus no mention of 2002 art 645. Was the author dodging a bullet?, Aimed at me? My interpretation of art. 645, with the required underfloor smoke detection and automatic air handler shutdown system, the above-mentioned caviot is not relevant in this case. And that is, Receptacles/plugs are allowed in the underfloor plenum areas, And the (UL) flexible appliance cords (less than 15') do not require plenum rating. It also does not help with table 400.4 does not list plenum rated flexible power cords.
Anybody else got a stance on this?
under raised flooring, and the following
appears on the scene. Note figure 1, and the following caviot. "not used for environmental air". Plus no mention of 2002 art 645. Was the author dodging a bullet?, Aimed at me? My interpretation of art. 645, with the required underfloor smoke detection and automatic air handler shutdown system, the above-mentioned caviot is not relevant in this case. And that is, Receptacles/plugs are allowed in the underfloor plenum areas, And the (UL) flexible appliance cords (less than 15') do not require plenum rating. It also does not help with table 400.4 does not list plenum rated flexible power cords.