Hi Everybody,

I need help in calculating the Actual chiller Load for a room if I am having the following data available with me.

Outside Wet Bulb :- 23, 24, 25, 26 Deg. C (I need to calculate at the given four temp.

Room Set Points :- Temp.= 31 Deg.C %RH= 45
Running Electrical Load = 1088 KW (Including Machine Load, Solar Load and Lighting Load)

Supply Air Volume = 250000 m3/Hr.

Please send me the working formula also because I need to understand the whole system and also I need to calculate for different Room Set Points also.

I will be very thankful to you.
 
Replies continue below

Recommended for you

The outside air wet bulb is indicative of the total heat in the outside air. Its impact will be on the cooling capacity and characteristics of an airhandler coil handling a mixture of return air and outside air.

If infiltration is part of your cooling load then, your cooling system will also have to respond to an increased heat content in that outside air.

For starters, try reading up on pyschrometrics, you could try this FAQ by Yorkman
Maybe some trane rep is trying to get you to spec his chillers, hit him up for their laaminated pyschrometric chart, has some useful instructions on the back.

You should be consulting with a mechanical colleague. Your question is analogous to a mechanical engineer posting to figure out a capacitor bank needed to improve the power factor of a factory.

Take the "V" out of HVAC and you are left with a HAC(k) job.
 
Is that school stuff? Sheesh... Guess I should go to school!
At least I understood the pyschometric stuff.... but the mechanical guru thing? HHmmmmm just thinking pyschometric made my head hurt more....