Hi,
I am designing a combined footing based on ACI 318-14 using STAAD Foundation Advance. Upon checking the calculation sheet (see attached file) from the software, I couldn’t figure out how the following values were computed by the software:
1. One-way shear parallel to longitudinal dimension (1314.76kN) – page 08
2. Top surface distribution reinforcement moment (859.2245kNm) – page 10
Can anyone please explain how STAAD Foundation computes these values?

 
 https://files.engineering.com/getfile.aspx?folder=fe1c6e77-f493-4f69-98e6-3cc957fe2d52&file=Combined_Footing_(Engg_Forum).pdf
Replies continue below

Recommended for you

From within the software help go to Verification Manual and refer to section 5 which contain details of how the different values are calculated for the ACI code. If you still have questions, please reach out to Bentley technical support.
 