- Apr 3, 2018
- 76
Hi All,
Commercial buildout project in Florida - Florida Building Code 2014
I do minor MEP for our plans and we have a stickler as a plan reviewer. Long story short, we are doing a commercial buildout which was combining two units into one. In the middle of the reno the tenant changed his mind on having two units and only decided to take one of them. Resulting in needing an additional bathroom in the single space. Because the bathroom is now at the end of the sanitary line we have received a comment from the plumbing plan reviewer of:
"Drink fountain to drain down stream of the bath groups" See the attached clip of the existing riser, the new toilet is in red
The drinking fountain drain and sanitary was already done and is under slab. I have never heard of this requirement prior. Can anyone point me to the code that requires this?
I want to comply but I do not know how without ripping out the slab and completely redoing the space which is out of the question. If we reroute the drinking fountain to the closest sink then wouldn't it be still not meet the downstream requirement? And what about the sinks, do they need to be downstream too?
Another thought, I am thinking this requirement is due to health issues with a water fountain not having sewage backflow through the drain. If this is the case could a backflow be put in and that should resolve the issue?
Any comments or suggestions much appreciated! Thank you.
Commercial buildout project in Florida - Florida Building Code 2014
I do minor MEP for our plans and we have a stickler as a plan reviewer. Long story short, we are doing a commercial buildout which was combining two units into one. In the middle of the reno the tenant changed his mind on having two units and only decided to take one of them. Resulting in needing an additional bathroom in the single space. Because the bathroom is now at the end of the sanitary line we have received a comment from the plumbing plan reviewer of:
"Drink fountain to drain down stream of the bath groups" See the attached clip of the existing riser, the new toilet is in red
The drinking fountain drain and sanitary was already done and is under slab. I have never heard of this requirement prior. Can anyone point me to the code that requires this?
I want to comply but I do not know how without ripping out the slab and completely redoing the space which is out of the question. If we reroute the drinking fountain to the closest sink then wouldn't it be still not meet the downstream requirement? And what about the sinks, do they need to be downstream too?
Another thought, I am thinking this requirement is due to health issues with a water fountain not having sewage backflow through the drain. If this is the case could a backflow be put in and that should resolve the issue?
Any comments or suggestions much appreciated! Thank you.