billcasper5968
Electrical
- Feb 1, 2014
- 6
Our procedure to calibrate our WTI (AKM Qualitrol) is to subject it to a constant temperature say 30 deg C for 10 minutes. After which, we inject 1A for 1 hour and our indication should read 50 deg C. This means that for 1A injection the increase should be 20deg C (based on a given graph). Since we are new personnel assigned to the plant, we don’t know the logic of this procedure. This was just an instruction handed down to us.
My concern at this point is the actual reading of our WTI during operation is above 100 deg C. If the WTI is reading correctly since it was calibrated per the instruction we might have a problem with our 47MVA power transformers. However, I asked the old personnel at the plant and they informed me that it had been above 100 deg C for a long time now (years). From reading other posts, it would mean that our transformers should have degraded considerably at this condition (100 deg C winding temp). However, this is not manifested on the electrical test and DGA so I am concerned that it is our calibration procedure that has an error. I want to know your views on this.
My concern at this point is the actual reading of our WTI during operation is above 100 deg C. If the WTI is reading correctly since it was calibrated per the instruction we might have a problem with our 47MVA power transformers. However, I asked the old personnel at the plant and they informed me that it had been above 100 deg C for a long time now (years). From reading other posts, it would mean that our transformers should have degraded considerably at this condition (100 deg C winding temp). However, this is not manifested on the electrical test and DGA so I am concerned that it is our calibration procedure that has an error. I want to know your views on this.