This might be the wrong forum, but... here goes. Please re-post if you feel this better belongs elsewhere.
Guys I need a shove in the right direction on the fundamentals of tank vapor recovery systems. The system in question consists of fourteen API 650 atmospheric storage tanks, ranging in size from 1500 bbl to 7500 bbl, manifolded together into a header with the endpoint of the header going to the suction of a compressor. The gas is then compressed and sent off to be mixed with utility fuel gas and subsequently burned as fuel.
The job of the system is to (1) collect tank vapors that off-gas from the product in the tanks (14° API crude) since the tanks can't be vented to atmosphere due to permit conditions (can you guess where I live yet?
) (2) control the tanks’ pressure to prevent damage to tanks due to overpressure. This system has no makeup gas because the product off-gasses fast enough to prevent the pressure from dropping as the tank levels are dropped when pumping out. Gas composition is about 0.6 mole fraction CO2, 0.3 CH4, 0.14 H2S, with the remainder being C2+ (mostly C6+). The gas is saturated.
The system currently does not work well. There are frequently leaks from the tanks (aka “releases” - a Very Bad Thing – can you say: “Notice of Violation”?) from the P-V roof hatches, the compressor controls are not stable, i.e. it cycles back and forth from recycle to full load, flange leaks, etc.
The task before me is to redesign the system. Scope of the project is (1) Replace the entire CS piping system (laterals to each tank and the header) with SS due to corrosion – this is the easy part; (2) “fix” the controls so the system is stable, reliable, and prevents unwanted releases. There is the tough part.
Here is where I am stuck. I am not knowledgeable on how these things are controlled and properly set up. Is it better to use one large P-V control valve/regulator, somewhere in the header, with large diameter piping to reduce pressure drop, or should each tank have its own P-V valve/regulator? Wouldn't this make the piping system smaller at the expense of more valves to maintain? And wouldn't this method provide faster system response? Since I don't have makeup gas I can use a separate tank hatch on each tank for vacuum protection.
I think the compressor control issue is just that somebody has messed with the setpoints and the speed of the PID loops, but I need to check into that.
Any help/suggestions/pointed barbs are welcome. If you could point me to a fundamental reference, that would help a lot. I got the Fisher info off the web and that helped a little but I need something more fundamental.
Thanks!!!! Pete
Thanks!
Pete
Guys I need a shove in the right direction on the fundamentals of tank vapor recovery systems. The system in question consists of fourteen API 650 atmospheric storage tanks, ranging in size from 1500 bbl to 7500 bbl, manifolded together into a header with the endpoint of the header going to the suction of a compressor. The gas is then compressed and sent off to be mixed with utility fuel gas and subsequently burned as fuel.
The job of the system is to (1) collect tank vapors that off-gas from the product in the tanks (14° API crude) since the tanks can't be vented to atmosphere due to permit conditions (can you guess where I live yet?
The system currently does not work well. There are frequently leaks from the tanks (aka “releases” - a Very Bad Thing – can you say: “Notice of Violation”?) from the P-V roof hatches, the compressor controls are not stable, i.e. it cycles back and forth from recycle to full load, flange leaks, etc.
The task before me is to redesign the system. Scope of the project is (1) Replace the entire CS piping system (laterals to each tank and the header) with SS due to corrosion – this is the easy part; (2) “fix” the controls so the system is stable, reliable, and prevents unwanted releases. There is the tough part.
Here is where I am stuck. I am not knowledgeable on how these things are controlled and properly set up. Is it better to use one large P-V control valve/regulator, somewhere in the header, with large diameter piping to reduce pressure drop, or should each tank have its own P-V valve/regulator? Wouldn't this make the piping system smaller at the expense of more valves to maintain? And wouldn't this method provide faster system response? Since I don't have makeup gas I can use a separate tank hatch on each tank for vacuum protection.
I think the compressor control issue is just that somebody has messed with the setpoints and the speed of the PID loops, but I need to check into that.
Any help/suggestions/pointed barbs are welcome. If you could point me to a fundamental reference, that would help a lot. I got the Fisher info off the web and that helped a little but I need something more fundamental.
Thanks!!!! Pete