Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Need help with t-min calculation on above ground storage tank

Status
Not open for further replies.

Leon Charles

Industrial
Jan 27, 2020
5
I'm having trouble with the t-min calculation for an above ground storage tank.
I followed instructions in API 653, but the final answer does not look correct, see below.

Tmin-?
D - 28.5'
G - 1.00
S - 24,900
E - .100
H - 45.9'-1 = 44.9'

Tmin = 2.6(H-1)DG/SE

Tmin = 2.6 x 44.9' x 28.5 x 1.00 = 3327.09 = 1.336
24,900 x .100 = 2,490

This t-min does not look correct because shell course #1 thickness is .250", sketch plate is .250" and and remaining floor is .312"
 
Replies continue below

Recommended for you

Dear Leon Charles,

All dimensions are in feet. What is the unit for 'S' ?

Regards.



DHURJATI SEN
Kolkata, India

 
Dear Leon Charles,

You made me calculate after so many years.

Take E = 1, you get t[sub]min[/sub] as 0.133"

Regards.




DHURJATI SEN
Kolkata, India

 
Dear Dhurjati Sen,
your answer to my t-min Question was very helpful.
Thanks,
Leon Charles.
 