SETUP:
32 pumps
480V, 16A, 3 ph, 10hp (from vendor, not sure if it makes sense......p = vi sqrt3 = (480V)(16A)(1.73) = 13286.4 VA
13286.4 VA / 746 W/hp = 17.8 hp, right?)
Assuming V & A correct:
(13286.4 VA x 1.25 safety) / pump x 32 pumps = 16608 VA x 32 = 531,456 VA = 532 kVA
Looking at generator rating, 3 ph:
82 kVA, 480 V, 98.6 A, 0.8 pf
Is it as simple as 98.6 A (generator rating) / 16 A (pump rating) = 6.1625 pumps per generator, so, 6 generators needed
OR
532 kVA / 82 kVA = 6.49 pumps per generator, so, 6 generators needed, again
As you can see, I am not an electrical engineer nor an electrician. Can anybody help with the proper approach and solution?
Thank you all in advance.