rockman7892
Electrical
- Apr 7, 2008
- 1,174
I noticed on one of the distribution relays on our 4.16kV plant distribution system a negative sequence current reading. The current on the entire distribution system was running at about 2500A and I noticed that there was a negative sequence current of about 75A. I realize that this negative sequence current comes from unbalanced voltages, and the voltage unbalance voltage reading was at 0.4%.
What is a negative sequence current value that should deemed as unaccaptable or as a maximum. Is this negative sequence current strictly a functin of voltage unbalance or load unbalance. 75A out of 2500A is about 3% so this seems to line up with the voltage unbalance. If that is the case is 0.4% voltage unbalance cause for any alarm?
What is a negative sequence current value that should deemed as unaccaptable or as a maximum. Is this negative sequence current strictly a functin of voltage unbalance or load unbalance. 75A out of 2500A is about 3% so this seems to line up with the voltage unbalance. If that is the case is 0.4% voltage unbalance cause for any alarm?