Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Negative Sequence Reactance

Status
Not open for further replies.

whycliffrussell

Electrical
Jul 10, 2006
92
why is the negative sequence reactance different than the positive sequence reactance for rotating machines?
 
Replies continue below

Recommended for you

Could it be because the rotor and the stator field rotate in opposite directions?
 
Negative sequence currents arise whenever there is unbalance in the system. A negative sequence component produces a resultant reaction field which rotates counter to the DC field system and a flux which cuts the rotor at twice the rotational velocity. This therefore induces double frequency currents in the field system and the rotor body. This effect is not present in the balanced system and accounts for the difference between positive and negative phase sequence reactances quoted by manufacturers.
Regards
Marmite
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor