negative sequence Vs zero sequence for ground fault

Status
Not open for further replies.

dfdt

Electrical
Sep 10, 2002
118
Can we use negative sequence current to detect ground faults on ungrounded system?
 
Replies continue below

Recommended for you

For single line-to-ground fault, the three sequence networks are in series, so I1=I2=Io= 0 for ungrounded system. In reality there is a small current due to capacitive coupling to ground.
 
Thanks DPC,and what i understand that there won't be any sequence current to rely on for detecting ground fault (which mainly would line capacitive discharge current)
 
What are key criterion for setting negative sequence current setting for detecting EF on grounded system? Like would tranposition of line interfere with/encroach on the setting value?
 