Were in the middle of designing a sanitary lift station. the lift station is built down approximately 38 ft. For the sump pit they excavated down and sloped down at a normal 1/1 ratio. Originally we were going to use concrete piles although because they are back filing the area that we are piling it introduces a negative skin friction force. Our piles are required to resist 65 kips which is regularly not a large load.
Now from my research/understanding, negative skin friction occurs when the settlement of the soil is greater that the settlement of the pile inducing a down-drag force on the pile. Me and another engineer at my firm determined that if the soil was properly compacted to 98% SPT then there should be no negative skin friction on the pile. We further talked about this with the geotechnical engineer that has been dealing with the soils and were told that absolutely negative skin friction cannot be ignored whether compacted or not. We have now changed the design to screw piles to reduce the diameter of the pile therefore reducing the skin friction.
Soil testing was done of the soil (not compacted) and we were given -50psf for the negative skin friction. For the force required we ended up designing a pile that could withstand 242kips (total) while most of its capacity was taken from negative skin friction.
Is there something more efficient than this that can be done/ could anyone comment on the geotechnicals stance on the matter.
Now from my research/understanding, negative skin friction occurs when the settlement of the soil is greater that the settlement of the pile inducing a down-drag force on the pile. Me and another engineer at my firm determined that if the soil was properly compacted to 98% SPT then there should be no negative skin friction on the pile. We further talked about this with the geotechnical engineer that has been dealing with the soils and were told that absolutely negative skin friction cannot be ignored whether compacted or not. We have now changed the design to screw piles to reduce the diameter of the pile therefore reducing the skin friction.
Soil testing was done of the soil (not compacted) and we were given -50psf for the negative skin friction. For the force required we ended up designing a pile that could withstand 242kips (total) while most of its capacity was taken from negative skin friction.
Is there something more efficient than this that can be done/ could anyone comment on the geotechnicals stance on the matter.