Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Negative terminal strip corrodes rapidly 1

Status
Not open for further replies.

zaphod1

Electrical
May 7, 2003
46
Hi, I thought this might be the best place to begin my quest. We have an electrical room in a waste-water facility that stays relatively clean and dry- yet quite often (monthly) there is a growth of a white, almost calcium looking, substance that covers all the terminals that are common with the negative of a 24Vdc power supply. The power supply is a standard 120Vac/24Vdc switching supply. Does anyone have an Idea?
Thanks
 
Replies continue below

Recommended for you

Congratulation, you made Aluminum oxide!
So take your Acid batteries out or vent the room.
And also use a dust mask the next time you work on the BUS.
 
Thanks for the response- but to clarify- there are no batteries in this room or in this system.
 
No UPS or any other chemical tank nearby?
(Alum, pH buffer, agglomeration solution)
 
Nope, nothing but a very foul odor. (it's a waste water treatment plant). That being said- I guess there is a possibility of fumes from the process entering the room, but this is the only thing that appears to be affected.
 
One additional thing- all copper turns black in the panels very quickly. There is some new wiring that was added late this summer that are already black.
 
Take a second look and look for HNO3 solution.
Is the room located in a low elevation point?

As a preventing act add a small blower that will induce fresh air from a high elevation.
 
Waste waster. Rotten egg smell. Hydrogen sulfide reacts with copper to form black corrosion and aluminum to form white corrosion. Humidity is also a requirement.
 
Good call by Compositepro.

Been there, seen that.

Good on ya,

Goober Dave
 
Yes that was a good response- I am sure that H2S explains the problem- however it leads to other questions- Why is it white corrosion on copper terminals and why only the negative terminals?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor