dominar
Electrical
- Jul 26, 2008
- 11
We have a motor control center (MCC) that has 8 - 480V Nema size 6 starters (FVNR). These starters control 8 - 400 HP motors with a KVA code of 'G' and is high efficiency rated. The motors are started Across-the-line (480V). The Full Load Current (FLA) for a motor is 418 amps and has a locked rotor amp (LRA) rating of 2900 amps. The motors are connected to natural gas compressors. High efficiency motors can be as high as 13 times FLA. The vendor says that they sized the Nema 6 starter per the KVA code 'G' that is on the motor's name plate.
The start up current was measured by the vendor to be 4603 amps for about 17ms, then it drops down below 2900 amps within 4 cycles about 80ms. The voltage dropped from 489 volts to 441 volts with a frequecny of 59.8 Hz. With the motor un-coupled from the compressors, the start up current was 3221 amps which is within Nema 12.36 that allows 1.8 - 2.8 times the 2900 LRA.
From time to time the contactors will weld together and has to be pulled apart and there is pitting of the contactors. The vendor says that this is normal, but I do not think so. The life cycle of these contactors will be significantly reduced. The vendor sites Nema IC 2-2000 (Performance Requirements and Tests section) that says the contactors meet the 10 times the FLA of the motor (code 'G') on the name plate for 0.1 seconds.
We found after testing that 1 set of 350MCM was run instead of 2 runs of 350MCM cable. Since the addition of the 2nd run of 350MCM, we have not seen any welding of contact, but we still get the high inrush currents.
The vendor does not want to address this issue and continues to skirt this issue. I know that soft starts or oversizing the contactors to Nema 7 are solutions, however, they are cost prohibitive right now.
Would anyone on this forum have any input or other solutions?
The start up current was measured by the vendor to be 4603 amps for about 17ms, then it drops down below 2900 amps within 4 cycles about 80ms. The voltage dropped from 489 volts to 441 volts with a frequecny of 59.8 Hz. With the motor un-coupled from the compressors, the start up current was 3221 amps which is within Nema 12.36 that allows 1.8 - 2.8 times the 2900 LRA.
From time to time the contactors will weld together and has to be pulled apart and there is pitting of the contactors. The vendor says that this is normal, but I do not think so. The life cycle of these contactors will be significantly reduced. The vendor sites Nema IC 2-2000 (Performance Requirements and Tests section) that says the contactors meet the 10 times the FLA of the motor (code 'G') on the name plate for 0.1 seconds.
We found after testing that 1 set of 350MCM was run instead of 2 runs of 350MCM cable. Since the addition of the 2nd run of 350MCM, we have not seen any welding of contact, but we still get the high inrush currents.
The vendor does not want to address this issue and continues to skirt this issue. I know that soft starts or oversizing the contactors to Nema 7 are solutions, however, they are cost prohibitive right now.
Would anyone on this forum have any input or other solutions?